CAN Communication Details for 699.H10 and 699.H11

Could you please provide the CAN communication details for the 699.H10 and 699.H11 products?

Specifically, we would like to confirm:

The CAN message IDs used for current/voltage feedback and current setpoint commands for each product, whether the current setpoint message needs to be transmitted cyclically, and the required transmission period or timeout behavior, the maximum supported current setpoint and what happens if a higher value is commanded.

Thanks!

699.H10 => Tx message: 0x18FFE3C1 (Current and voltage feedback)
Rx message: 0x18FFE203 (Current set point)

699.H11 => Tx message: 0x18FFE1C0 (Current feedback)
Rx message: 0x18FFE003 (Current set point)

The messages sent to determine the set point values for both product must be transmitted cyclically every 100ms. If the messages are received after more than 100ms, the current outputs will be turned off.

Our product provide a maximum 2.5A. Therefore, even if a value greater than 2500 is sent as the set point, the product will limit itself to the maximum set value.